Oh wow, I’d completely forgotten about zwave tweaker. I had it installed so that must have been what I used for this thing previously.
So I got this message from geeji in another thread:
from geeji:
First I assume that you have properly checked (see above in this thread) that you DO have a ZW5 version of the FGK-101. Parameters involved differ between pre-ZW5 and ZW5 versions.
Second, “to provide near real time temperature updates”, assuming you don’t care about power consumption, you just need to adjust 2 parameters : #50 [Interval of temperature measurements] and #51 [Temperature reports threshold [1/10th °C]].
Parameter #52 [Interval of temperature reports] is just overkill unless you do have COMPLETELY stable temperature, which is unlikely is you set, for instance, Parameter #51 down to 1.
AFAIU what you try to achieve, I would just set parameter #50 down to 1 mn = 0x003C (line 753 in JJ’s Fibaro FGK-10x ZW5 Handler v0.9.7.21), and parameter #51 down to 0.1°C = 0x0001 (tempQuantumTenth=1, lines 561 & 741).
Note that I never tested so low values, and that the ZW5 version of the FGK-101 has way too many bizarre bugs…
Using this as a guideline, here’s what’s working for me. I’m using the JJ FGK-10x DH with the following params set in the code on lines 751-755 or so:
parameter 50: 0x05
parameter 51: 1
parameter 52: 0x05
I’m now seeing updates of as little as .1F at intervals as low as 4 seconds. That’s basically what I’m looking for from the z-wave device. I’m not sure the sensor itself is sensitive enough however. It seems to take far longer to detect rising temps than falling.
so for example it takes nearly a minute to register this change from 86.7 to 112 when I’m running hot water on the sensor:
2018-03-30 2:38:38.547 PM PDT
moments ago DEVICE temperature 112.0 Hot Water Loop Temp temperature is 112.0°F
2018-03-30 2:37:44.180 PM PDT
moments ago DEVICE temperature 86.7 Hot Water Loop Temp temperature is 86.7°F
whereas this change from 105.0 to 104.6 takes only 7 seconds as it cools:
2018-03-30 2:39:27.167 PM PDT
moments ago DEVICE temperature 104.6 Hot Water Loop Temp temperature is 104.6°F
2018-03-30 2:39:20.829 PM PDT
moments ago DEVICE temperature 105.0 Hot Water Loop Temp temperature is 105.0°F
Either this has to do with the limitations of the sensor itself, or I’m reporting at TOO HIGH of an interval such that as new reports come in they’re cancelling older ones and it doesn’t report the higher state until it stabilizes? It would be so much more useful if you could see the temp run up like you can see it run down.